MyHome OpenWebNet Via LAN Interface
From Domoticz
Revision as of 23:13, 14 May 2020 by Spugno (talk | contribs) (Created page with "== Overview == Open Web Net is a language through which it is possible to exchange data and send commands between a remote unit and the BTicino My Home system. The protocol is...")
Overview
Open Web Net is a language through which it is possible to exchange data and send commands between a remote unit and the BTicino My Home system. The protocol is thought to be independent of the means of communication used, considering as a minimum requirement the possibility of being able to use DTMF tones on the normal PSTN telephone line. This language was also designed to allow devices such as PCs, Smartphones and tablets to communicate with the My Home system remotely. The Open Web Net was introduced to provide an abstract level that allows the supervision and control of My Home systems focusing on the functions without caring about the details of the installation and without having to know the SCS technology.
Detailed information can be found on the manufacturer site: [1]
Myhome gateway support
Domoticz supports both official and unofficial gateways. The supported devices are:
  • F454 Web Server A/V
  • MyHome Server1
  • MyHome Screen 3.5"(eg. LN4890)
  • MyHome Screen 10"
  • MH202 Scenario programmer
  • others not yet tested ..
Myhome gateway authentication
Authentication can be performed in 3 ways:
  • Without password, via IP of the device within the IP range enabled in the gateway
  • With numeric password (at least 5 characters) for unofficial gateways that require a hash calculation
  • With alphanumeric password (from 5 to 16 characters) for the gateways that implement HMAC authentication (eg MHS1 or F454 with the HMAC option enabled)
Domoticz integrated OpenWebNet support
The OpenWebNet protocol is now partially supported out-of-the-box in the current version.
  • Setup -> Hardware.
  • Configuration:
    • Model: select 'MyHome OpenWebNet with LAN interface'.
    • Remote addess: set the ip of your OWN gateway.
    • Port: set default 20000, or your personalized port.
    • Rate Limit: set the seconds between the complete scans of your system. Set 0 to disable continuous scanning. If there are many devices in the system, it is advisable to leave this value at 0.
    • Date/time synchronization (available with stable version > 2020.2): set the minutes between the date / time synchronization checks. Set 0 disable the synchronization of your Bticino domotics system.
    • User name: used only with HMAC authentication
    • Password: from 5 to 16 alphanumeric characters (for unofficial gateways must be a numeric password).
  • Press Add.
  • At the first connection, the system will be scanned and the supported devices will be created automatically*.
  • Setup -> Devices will show all the newly added devices.
*Some devices, such as dry contacts and temperature probes, are added only when they spontaneously update their status. This means that before they are visible in the device list you have to wait for the first event captured by the connection in monitor mode.
Manual addition of devices
Some types of devices can also be added manually. These devices are:
  • lights
  • blinds
  • auxiliary contacts
To do this it is necessary:
  • go to Switches -> light / manual switch
  • Select your OpenWebNet Hardware
  • Select the switch type you want
  • Select the model:
    • 'Lights OpenWebNet Bus'
    • 'Blinds OpenWebNet Bus'
    • 'Auxiliary OpenWebNet Bus'
    • 'Dry Contact OpenWebNet Bus'
    • 'IR Detection OpenWebNet Bus'
    • 'Custom OpenWebNet Bus'
  • Select the area code and light point of the device you want to add
  • Then add device
OpenWebNet message
An OpenWebNet message is structured with variable length fields separated by the special character '*' and closed by '##'.
The characters admitted in the fields are numbers and the character “#”.
Fields Description
WHO home automation system function to which the OpenWebNet message is referenced
(example WHO = 1 for the messages for lighting system management)
WHAT an action to do or a status to read. For every WHO there is a specific WHAT table.
(example of actions/status: switch OFF light, active alarm ..)
WHERE the set of objects to which the OpenWebNet message is referred.
It can be a single object, a group of objects, a specific environment, the entire system, etc.
For every WHO (and therefore for every function) there is a specified WHERE table.
DIMENSION a range of value of the dimension of the object to which the message is referred.
For every WHO (and therefore for every function) there is a specific DIMENSION table.
VALUE the read/written value of a written/required/read dimension
The following table shows the different types of messages that can be sent and received within an Open Client-Server conversation.
Message Type Format
ACK *#*1##
NACK *#*0##
Command / Status *WHO*WHAT*WHERE##
Status Request *#WHO*WHERE##
Dimension Request *#WHO*WHERE*DIMENSION##
Dimension Read *#WHO*WHERE*DIMENSION*VALUE1*...*VALUEn##
Dimension Write *#WHO*WHERE*#DIMENSION*VAL1*VAL2*...*VALn##
Domoticz OpenWebNet WHO support
The WHOs supported or not are listed below:
Description WHO Code Support
SCENARIO 0 not supported
LIGHTING 1 supported
AUTOMATION 2 supported
LOAD CONTROL 3 not supported
TEMPERATURE CONTROL 4 supported
BURGLAR_ALARM 5 supported
DOOR ENTRY SYSTEM 6 not supported
AUXILIARY 9 supported
GATEWAY INTERFACES MANAGEMENT 13 supported
SCENARIO SCHEDULER SWITCH 15 not supported
SOUND DIFFUSION 16/22 not supported
SCENARIO PROGRAMMING (MH200N) 17 not supported
ENERGY MANAGEMENT 18 supported
CEN PLUS DRY CONTACT IR DETECTION 25 supported
Device description
The devices are automatically added via bus scan commands and subsequent feeedback on the monitoring connection. Each device uses an ID made up of WHO and WHERE (as far as possible and compatible with Domoticz). In addition, only certain types of devices can be added manually. All the types of devices present are described below.
Lighting (WHO = 1)
This device is added as a general switch, below is an example of ID construction:
Lighting message: *1*0*42##
WHO = 1
WHAT = 0 (OFF)
WHERE = 42 (AREA = 1 + POINT = 7)
The ID consists of an 8 hexadecimal digit number composed as follows:
ID = (WHO << 16) || WHERE
In this example we have:
ID = (0x0001 << 16) | 0x002A = 0001002A
NOTE: when a device with a specific area is added, an additional AREA type device is added. This new device can control all the lights associated with the same area.
Automation (WHO = 2)
Automation message: *2*2*92##
WHO = 2
WHAT = 2 (DOWN)
WHERE = 92 (AREA = 9 + POINT = 2)
ID = (0x0002 << 16) | 0x005C = 0002005C
Temperature Control (WHO = 4)
This device is added as a temperature device, below is an example of ID construction:
Temperature control message: *#4*5*0*0244##
WHO = 4
WHERE = 5 (N = 5 + S = 0)
DIMENSION = 0
VALUE = 0244 (24,4 °C)
The ID consists of an 4 decimal digit number composed as follows:
ID = (WHO << 12) || WHERE
ID = (4 << 12) | 5 = 4005
Burglar Alarm(WHO = 5)
This system add some devices with fixed ID witohu WHO information:
ID Device description
1 - 8 Alarm sensor zone
17 System status
18 Network status
19 Battery status
20 System engagement
Alarm Control with Auxiliary
With the myhome system it is possible to monitor the alarm system status, but it cannot be controlled directly via the OpenWebNet protocol. The only possibility is to use AUXILIARY devices, configuring your alarm control panel to execute some commands (eg Activate alarm) when it receives a particular auxiliary OpenWebNet command.
Automation must be configured via a special alarm system menu. Automations allow you to run an OPEN command when a particular event occurs. In this case, the events are the changes of state of the auxiliary device (who = 9) and the command to be performed is a burglar alarm command(who = 5).
Configuration Automation 1: when AUX-1 go OFF, then DISENGAGE all Zones
Name: Disengaged all zones
Event: command OPEN = *9*0*1##
OPEN command to execute: *5*9##
Configuration Automation 2: when AUX-2 go ON, then ENGAGE active Zones
Name: Engaged active zones
Event: command OPEN = *9*1*2##
OPEN command to execute: *5*8##
Configuration Automation 3: when AUX-3 go ON, then ENGAGE Zone 1 and Zone 4
Name: Engaged zone 1 and zone 4
Event: command OPEN = *9*1*3##
OPEN command to execute: *5*8#14##
Now it is possible to create auxiliary devices in domoticz through the manual procedure, first of type 'push OFF button' and the others of type 'push ON button'.
Alarm notification by LUA script
Here is a LUA script to receive some notifications. It is only necessary to change the name of the devices:
"Home alarm status" 'Alarm Zone 1' .. 'Alarm Zone N' 'Battery status' "Network status"
with those of your devices.
 if devicechanged then
    for deviceName,deviceValue in pairs(devicechanged) do
        -- Alarm Engagement
        if (deviceName=='Home Alarm Status') then
            print(deviceName.. ': ' .. deviceValue)
            if deviceValue == 'Engaged' then
                commandArray['SendNotification']='Alarm Engaged'
            elseif deviceValue == 'DisEngaged' then
                 commandArray['SendNotification']='Alarm DisEngaged'
        -- Alarm sensor zones
        if (deviceName=='Alarm Zone 1') or (deviceName=='Alarm Zone 2')) then
            print(deviceName .. ': '.. deviceValue)
            if (deviceValue == 'Intrusion') then
                commandArray['SendNotification']="Intrusion ON#" .. deviceName
            else --if ((deviceValue == 'Active') or (deviceValue == 'Inactive')) then
                commandArray['SendNotification']="Intrusion OFF#" .. deviceName
        -- General system status alarm
        -- if (deviceName=='Alarm System Status') then
        -- end
        -- Alarm battery status
        if (deviceName=='Battery Status') then
            if deviceValue == 'Battery Ok' then
                commandArray['SendNotification']='Battery is OK'
            elseif deviceValue == 'Battery Fault' then
                commandArray['SendNotification']='Battery is FAULT!'
            elseif deviceValue == 'Battery Unloads' then
                commandArray['SendNotification']='Battery is Unloads!'
        -- Alarm Network status
        if (deviceName=='Network Status') then
            if deviceValue == 'Network OK' then
                commandArray['SendNotification']='Network is OK'
            elseif deviceValue == 'No network' then
                commandArray['SendNotification']='No network!'
Auxiliary (WHO = 9)
Lighting message: *9*0*4##
WHO = 9
WHAT = 0 (OFF)
WHERE = 4 (AUX number)
ID = (0x0009 << 16) | 0x00004 = 0009004
NOTE: The auxiliary devices can be used to send commands to the alarm system if the alarm control unit (eg 3486) has been appropriately configured.
Gateway Interface Management(WHO = 13)
TODO
Energy Management (WHO = 18)
TODO
CEN Plus, Dry Contact and IR Detection (WHO = 25)
TODO
Custom Command
TODO
